Why would an RTD start to give a negative reading as temperature increases?
 
Replies continue below

Recommended for you

An RTD, by itself, cannot give a "negative reading" since it's only a resistor. It's the circuitry that measures the resistance and it's thermal compensation and temperature algorithm that produce a negative result, so I would look there, although, it's not impossible that the RTD is damaged somehow.

> Is the circuitry calibrated correctly?
> Is the thermal compensation correctly designed and calibrated?
> Is the RTD working correctly, in general?

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! faq731-376 forum1529 Entire Forum list
 
I suppose one could have an system that drives downscale on a detected RTD open circuit, So it might read OK at lower temp, but the thermal expansion causes it to go open circuit and the fault mode drives the indicated signal downscale.

One reported failure mode is shorted element coil winding producing an overall lower resistance element. But it would have a low offset, not a reversed temperature coefficient.

An increase in resistance (loose or corroded connection) in the 3rd wire of a 3 wire RTD circuit that does lead wire compensation drives the indicated temperature lower.

A water-flooded field junction box could conceivably reduce the excitation current from the AI circuit by losing some current through a ground loop fault. Highly theoretical circumstance, given how few direct connected RTD's are wired through field junction boxes.

Or it might not be an RTD, it might be some other temperature sensor.

Thermocouples connected "backwards" (wrong polarity) drive the indicated temperature in the wrong direction.

A typical Pt100 RTD has a positive temperature coefficient. A thermistor with a negative temp coefficient connected to a circuit expecting a positive coefficient sensor will drive the indicated temperature in the wrong direction.

Usually miswiring a 3 or 4 wire Pt100 or Pt1000 to its appropriate analog input will cause it to report an offscale value or a fault code.
 
Dear Mr. oosani (Electrical)(OP)16 May 22 19:11
"...Why would an RTD start to give a negative reading as temperature increases? "
1. The term RTD is generic for Resistance Temperature Detector. There are basically three different types with different R-T characteristics: viz a) PTC, b) NTC and c) thermistor. The PTC type with resistance increase with temperature. The NTC is the reverse of PTC. The thermistor exhibit a very small NTC regions until the temperature reaches the "switch" point. After the switch point, the resistance increase rapidly in PTC.
2. A RTD with NTC characteristic would decrease in resistance with increase in temperature.
3. BTW: A RTD does NOT change from PTC to NTC or (vise versa), [throughout its life]. Check the monitoring instrument if it changes the characteristic.