XR250
Structural
- Jan 30, 2013
- 5,951
I have 2800lb chiller that an owner wants to put on a roof (i-beams and metal deck)
As we are going to be installing the unit near a bearing wall, the roof structure has plenty of capacity to carry the weight.
The roof is metal deck w/ 5" polyiso and a membrane. The owner does not want to penetrate the membrane for support legs.
I proposed to lay down double 2x12 flatwise over the beams that carry 6x6 pt beams perpendicular that support the unit.
The 2x12's are intended to distribute the load over polyiso. Based on their surface area, I get a bearing pressure of less than 4 psi. The polyiso is reportedly has a 20 psi rating which, is my understanding, the load that will cause 10% deformation in the foam. Assuming a linear relationship, my load would cause 2% deformation or 1/10"
Does this sound like reasonable approach?
Thanks
As we are going to be installing the unit near a bearing wall, the roof structure has plenty of capacity to carry the weight.
The roof is metal deck w/ 5" polyiso and a membrane. The owner does not want to penetrate the membrane for support legs.
I proposed to lay down double 2x12 flatwise over the beams that carry 6x6 pt beams perpendicular that support the unit.
The 2x12's are intended to distribute the load over polyiso. Based on their surface area, I get a bearing pressure of less than 4 psi. The polyiso is reportedly has a 20 psi rating which, is my understanding, the load that will cause 10% deformation in the foam. Assuming a linear relationship, my load would cause 2% deformation or 1/10"
Does this sound like reasonable approach?