Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

RTU screens with gap below, snow still to pile? 1

Status
Not open for further replies.

Echo26

Structural
Dec 29, 2021
17
If you have RTU screens, snow could pile around the RTU screen but if you have a gap let's say 2'-0", wouldn't that change snow piling. Snow will hit the upper portion of the screen, but the wind could blow it off so is it safe to say that there won't be snow piling. Is there a commentary in the building code where it covers this type of roof obstruction?
 
Replies continue below

Recommended for you

I don't follow the sketch. What code are you looking for answers from? ASCE 7 has some provisions for snow loading on open structures which might be the closest to what you are describing.
 
ASCE 7-16 has provisions that define the vertical clearance required in order to ignore drift loads.
I believe that it's 2' (or maybe 3') above the flat roof snow height.

This snow could still drift against the RTU inside the enclosure. If you meet the height requirements, I`d ignore the enclosure when applying drift to the unit.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor