I am looking for any data on past projects or general rules of thumb for block load estimating: cooling, heating and ventilation. The project is located in Illinois and is a skilled nursing facility. This is my first project of this type of occupancy, and I want to check my preliminary loads. If anyone knows where I could possibly go to find this type of information, or can give me advice from personal experience, I would appreciate any help. My experience tells me to use around 65 BTU/SF (because of increased O.A. requirements),250 SF/ton, and 9 A/C.
 
Replies continue below

Recommended for you

I am compling a list of "Rules of Thumb" for HVAC design - mostly for estimated design cost, but also checking program output results.

Some of the Rules of Thumb include for cooling: ~300 SF/Ton external spaces and ~400 SF/ton internal spaces (~600 SF/ton for residential). These can vary by +/- 50 to 75 SF/ton, depending on the actual application.

For heating it seems that ~35 BTU/hr-SF is a good gage. However, there is also a pretty fair variance on this Rule of Thumb also.

I am finding out that these Rules of Thumb are good to get in the ball park, however, only experience can get you to the best solution that will work.
 

For your weather and for the application you have I believe 250 sf/ton is too conservative. I think it should be in the range of 285-300 sf/ton [sig][/sig]
 