Dear guys we have some motors which were originally winded on delta with a rated voltage of 230 vlots 3 phase but our winder has changed the motor's internal connection to star( using the same original winding wire) so we can run the same on 400 volts to meet our system requirements.The motors are running fine on the new voltage but I have some questions which I would like you guys to reply.
1- The motor rated current was 8.5 ampere at 230 volts 3ph 50hz and the rated KW were 2.2 as we have changed the winding to star connection and running it at 400 volts now what would be the normal/safe current for this motor?
The motor is taking 5.5 ampere on load while the no load current is around 4 ampere at new voltage.I assume that the same motor can be run safely at around the same rated current i.e 8 ampere or so because the winding wire remains original.Kindly give your valueable comments.
regards
1- The motor rated current was 8.5 ampere at 230 volts 3ph 50hz and the rated KW were 2.2 as we have changed the winding to star connection and running it at 400 volts now what would be the normal/safe current for this motor?
The motor is taking 5.5 ampere on load while the no load current is around 4 ampere at new voltage.I assume that the same motor can be run safely at around the same rated current i.e 8 ampere or so because the winding wire remains original.Kindly give your valueable comments.