Hi, just returned from a (hitherto) not so successful attempt to run an externally excited 10 kV synchronous motor from a 500 V + transformer frequency inverter. The set up is used only to accelerate the motor (instead of a pony motor) with no load coupled to the output shaft. We had our doubts as to the possibility to have a stable operation all the way from 0 Hz to the 53 Hz needed. And our anticipations were met - and more. Right now, we have been able to run up to about 12 Hz, then there is a violent oscillation and the drive shuts down because of high DC link voltage (comes from acc/ret action caused by oscillations).
We are running a pure scalar inverter with no frequency controller. Everything the inverter is supposed to do is output a frequency and an almost proportional voltage (we use a 2 % boost decreasing to 0 % at 10 Hz).
Any experience out there? Tips? (If I might say so; spare the P and I tips for the non-existing controller). It is a pole angle oscillation we are getting and not a controller instability. There are no amortisseur windings and no other damping in the motor.
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
We are running a pure scalar inverter with no frequency controller. Everything the inverter is supposed to do is output a frequency and an almost proportional voltage (we use a 2 % boost decreasing to 0 % at 10 Hz).
Any experience out there? Tips? (If I might say so; spare the P and I tips for the non-existing controller). It is a pole angle oscillation we are getting and not a controller instability. There are no amortisseur windings and no other damping in the motor.