In a facility with a power factor penalty, the guys there thinking about running the emergency diesel generator in parallel with grid in a synchronous condenser mode.
Two ideas here:
1- Run the DG with low driving power to supply generator losses with full reactive power support.(Generator)
2- Run the DG to catch the synchronous speed of the generator then reduce the fuel intake with excitation. (Motor)
For the 2nd option, the reverse power protection setting should be modified to avoid tripping.
Economics, running a motor from grid is cheaper than using fuel and associated carbon tax.
I am not aware of issues rising from running diesel engine at low loading? is it possible to drive the diesel generator with no fuel?
I read somewhere online that overspeeding of diesel generator in case of motoring can damage the bearing, I wonder if the motor is synchronized to the grid, why would overspeeding happen?
Any clues?
Two ideas here:
1- Run the DG with low driving power to supply generator losses with full reactive power support.(Generator)
2- Run the DG to catch the synchronous speed of the generator then reduce the fuel intake with excitation. (Motor)
For the 2nd option, the reverse power protection setting should be modified to avoid tripping.
Economics, running a motor from grid is cheaper than using fuel and associated carbon tax.
I am not aware of issues rising from running diesel engine at low loading? is it possible to drive the diesel generator with no fuel?
I read somewhere online that overspeeding of diesel generator in case of motoring can damage the bearing, I wonder if the motor is synchronized to the grid, why would overspeeding happen?
Any clues?