ccfromtx
Electrical
- Apr 16, 2002
- 2
The inspector in our plant refuses to allow rupture disks that have a pressure rating at ambient that is greater than MAWP. I say that the ASME only requires that the rupture disk pressure rating is less than MAWP at the temperature it is expected to rupture. Our vendor always stamps the disk with the specified burst pressure and temperature and the burst pressure at ambient conditions.
Example:
A vessel has an MAWP of 200 PSIG at 300 Deg F. The operating conditions are 150 PSIG at 250 Deg F. The rupture disk is specified to burst at 200 PSIG at 250 Deg F. When the disk is received from the vendor the disk will be stamped 197 PSIG (due to manufacturing tolerance) at 250 Deg F and at 215 PSIG at 72 Deg F. Our inspector will reject this disk because of the 215 PSIG rating at ambient.
I think our inspector is wrong, can anybody give me supporting evidence? Also, can anybody tell me why the vendor stamps with both the specified and ambient conditions. I know the vendor has to test at ambient but why stamp the disk?
Example:
A vessel has an MAWP of 200 PSIG at 300 Deg F. The operating conditions are 150 PSIG at 250 Deg F. The rupture disk is specified to burst at 200 PSIG at 250 Deg F. When the disk is received from the vendor the disk will be stamped 197 PSIG (due to manufacturing tolerance) at 250 Deg F and at 215 PSIG at 72 Deg F. Our inspector will reject this disk because of the 215 PSIG rating at ambient.
I think our inspector is wrong, can anybody give me supporting evidence? Also, can anybody tell me why the vendor stamps with both the specified and ambient conditions. I know the vendor has to test at ambient but why stamp the disk?