Sdpaddler50
Mechanical
- Aug 30, 2012
- 200
S-1, Type III-N, rack storage Class I-IV, but also fairly large amount of Group A, unexpanded plastics.
-Sprinkler protection (ceiling only) adequate for the Class I-IV per engineering analysis I did.
-Sprinkler protection is not adequate for the plastics – shocker. They will either need to reinforce the ceiling, or add in-rack sprinklers. This would then be a separate area, and controls put in place to store the nasty plastics here only. I know this has its own inherent challenges, but I believe this operator has the ability to manage it because these are distinct products lines.
Per Cal Fire Code 2010
2304.2 Designation based on engineering analysis. The designation of a high-piled combustible storage area, or portion thereof, is allowed to be based on a lower hazard class than that of the highest class of commodity stored when a limited quantity of the higher hazard commodity has been demonstrated by engineering analysis to be adequately protected by the automatic sprinkler system provided. The engineering analysis shall consider the ability of the sprinkler system to deliver the higher density required by the higher hazard commodity. The higher density shall be based on the actual storage height of the pile or rack and the minimum allowable design area for sprinkler operation as set forth in the density/area figures provided in NFPA 13. The contiguous area occupied by the higher hazard commodity shall not exceed 120 square feet (11 m2) and additional areas of higher hazard commodity shall be separated from other such areas by 25 feet (7620 mm) or more. The sprinkler system shall be capable of delivering the higher density over a minimum area of 900 square feet (84 m2) for wet pipe systems and 1,200 square feet (111 m2) for dry pipe systems. The shape of the design area shall be in accordance with Section 903.
But, I, and client don’t want to be limited to storing the high hazard plastics to 120 sq ft piles. They have about 5,000 sq ft of plastics in racks to 18 ft high so this is not practical.
NFPA 13, 2013:
5.6.1.2.4 Mixed Commodity Segregation. The protection requirements for the lower commodity class shall be permitted to be utilized in the area of lower commodity class, where the higher hazard material is confined to a designated area and the area is protected to the higher hazard in accordance with the requirements of this standard.
I would assert that if the protection is improved for the plastics (in-racks for example) then we have succeeded in providing adequate protection per NFPA 13. From a practical sense, what is limiting the pile sizes, or providing 1 hour fire walls in between the lower hazard, and high hazard storage going to do, which is now adequately protected?
IE, my assertion is that the sprinkler system will control a fire involving the high hazard, so the provision of fire walls, and/or limiting pile sizes is not needed. But, when I go back to the fire codes, it is telling me otherwise.
For example – what if a brand new building goes up across the street, and they store group A plastic exclusively. As long as the sprinkler system is designed to protect the storage per 13, we don’t need any fire barrier walls there.
Has anyone been successful in taking this approach with the ahj to omit fire barrier walls, or pile size limiations? Any other ideas, or options are appreciated.
-Sprinkler protection (ceiling only) adequate for the Class I-IV per engineering analysis I did.
-Sprinkler protection is not adequate for the plastics – shocker. They will either need to reinforce the ceiling, or add in-rack sprinklers. This would then be a separate area, and controls put in place to store the nasty plastics here only. I know this has its own inherent challenges, but I believe this operator has the ability to manage it because these are distinct products lines.
Per Cal Fire Code 2010
2304.2 Designation based on engineering analysis. The designation of a high-piled combustible storage area, or portion thereof, is allowed to be based on a lower hazard class than that of the highest class of commodity stored when a limited quantity of the higher hazard commodity has been demonstrated by engineering analysis to be adequately protected by the automatic sprinkler system provided. The engineering analysis shall consider the ability of the sprinkler system to deliver the higher density required by the higher hazard commodity. The higher density shall be based on the actual storage height of the pile or rack and the minimum allowable design area for sprinkler operation as set forth in the density/area figures provided in NFPA 13. The contiguous area occupied by the higher hazard commodity shall not exceed 120 square feet (11 m2) and additional areas of higher hazard commodity shall be separated from other such areas by 25 feet (7620 mm) or more. The sprinkler system shall be capable of delivering the higher density over a minimum area of 900 square feet (84 m2) for wet pipe systems and 1,200 square feet (111 m2) for dry pipe systems. The shape of the design area shall be in accordance with Section 903.
But, I, and client don’t want to be limited to storing the high hazard plastics to 120 sq ft piles. They have about 5,000 sq ft of plastics in racks to 18 ft high so this is not practical.
NFPA 13, 2013:
5.6.1.2.4 Mixed Commodity Segregation. The protection requirements for the lower commodity class shall be permitted to be utilized in the area of lower commodity class, where the higher hazard material is confined to a designated area and the area is protected to the higher hazard in accordance with the requirements of this standard.
I would assert that if the protection is improved for the plastics (in-racks for example) then we have succeeded in providing adequate protection per NFPA 13. From a practical sense, what is limiting the pile sizes, or providing 1 hour fire walls in between the lower hazard, and high hazard storage going to do, which is now adequately protected?
IE, my assertion is that the sprinkler system will control a fire involving the high hazard, so the provision of fire walls, and/or limiting pile sizes is not needed. But, when I go back to the fire codes, it is telling me otherwise.
For example – what if a brand new building goes up across the street, and they store group A plastic exclusively. As long as the sprinkler system is designed to protect the storage per 13, we don’t need any fire barrier walls there.
Has anyone been successful in taking this approach with the ahj to omit fire barrier walls, or pile size limiations? Any other ideas, or options are appreciated.