bentov
Electrical
- Feb 2, 2004
- 74
Got a phone call describing the following system: 480/277 4W meter main, 100a fusible disconnect feeding 1 mile run as follows - 3x350MCM Al 1/2mi to 7.5hp 480V combination panel for 3-phase submersible pump in 16ft deep drainage collector; 3x2/0 Al next 1/4mi to identical setup; 3x#4 Al final 1/4mi to 3rd identical setup - the entire run is 3 wires only in PVC underground conduit. They drove ground rods at each pump location, connected to the panel bonding lugs & pump cable ground conductor. Sounds like it's a fairly new install by someone unfamiliar with NEC Article 250, either passed or didn't get an inspection.
Their question - exactly how unsafe is this, and how can it be made right? The obvious answer is to re-pull everything with the 4th conductor. If & until that gets done though, it's like the old ungrounded days I guess - 1st ground is "free", 2nd creates the line-to-line fault that blows a fuse. Meantime I'm trying to visualize the shock risk to personnel in contact with the panel, piping & water, how that relates to the significant distance back to the earth referenced utility transformer, whether those ground rods should be disconnected or not, etc. Can this be made safe with GFCIs only?
Their question - exactly how unsafe is this, and how can it be made right? The obvious answer is to re-pull everything with the 4th conductor. If & until that gets done though, it's like the old ungrounded days I guess - 1st ground is "free", 2nd creates the line-to-line fault that blows a fuse. Meantime I'm trying to visualize the shock risk to personnel in contact with the panel, piping & water, how that relates to the significant distance back to the earth referenced utility transformer, whether those ground rods should be disconnected or not, etc. Can this be made safe with GFCIs only?