skltkis

Chemical
May 11, 2016
2
Hi,

I want to know what is the safety distance that needs to be maintained between ammonia compressor and the electrical substation.
 
Replies continue below

Recommended for you

Check NFPA 55 or Compressed Gas Association G-2.1. Unfortunately, I don't believe either has a specific requirement that prescribes a separation distance from a NH3 compressor or stationary container and an electrical substation.
 
Although there may not be any prescribed distances, I would still use some safe engineering judgment. While anhydrous ammonia is not considered a flammable liquid, under the right oxidizing condition, it will combust; it also has a high affinity for water which can be dangerous. You may want to check Mass. CMR on Refrigeration/AC as it may have additional info as this State has a two year mandatory inspection on related equipment over 20 tons. For lack of guidance, you could adopt NFPA 70 discussing safe distances from flammable and combustible liquid storage.
 