MRM
Geotechnical
- Jun 13, 2002
- 345
Here's the scenario; there is a site with a 10 foot +/- tall earth embankment. Although the embankment has been stable for the last 30 years, numerous seeps were observed a few years ago. Soil borings were completed in the area at the time the seeps were observed. The geology in the area is complex, with alternating silty clay and water-bearing sandy strata to depth. It is believed that several discrete aquifers exist within these soils. Some of these aquifers are artesian, while others represent the regional groundwater flow towards the bay about 800 feet away.
Now, to provide room for a new development, the embankment will be replaced with a new reinforced segmental retaining wall.
A contractor came in and installed a sheet pile wall (believed to be about 20 feet in length), along with 2 inch PVC well points (believed to be about 20 feet long, screened on the bottom 5 feet) on the side of the sheet wall opposite of the proposed excavation for the new segmental wall. The location of the sheet wall was near the crest of the existing embankment at the top. The wells were installed by jetting in under high water pressure on approximate 3 to 4 feet centers. Prior to the pump being turned on, some artesian flow was observed in about 50% of the wells. This was not surprising based on the original soil boring information.
After the pump had been started and was running for a few days, the contractor excavated the area adjacent to the sheet pile wall down approximately 8 to 10 feet. They noticed that even with the pumps running, there were sand boils at some areas near the wall, and the area of the proposed retaining wall was generally wet.
We were called out to the site to help them understand why their dewatering system was not working. First of all, it was obvious to me that the well points were not doing the job for which they were intended. I believe the well points are probably pulling water from deeper aquifers that probably do not need to be dewatered in order to dry the site up. There are more shallow aquifers making it through and up and around the sheet wall that are not affected by the well points.
My opinion about the sand boils is this; while they may be result of natural discontinuities in the soil strata that are now exposed to air for the first time, I believe that the pressure of the jets may have aggravated the problem by weakening certain strata and ultimately causing more sand boils to form during excavation in that area than would have existed otherwise. What do you think of that? In your experience, have you seen the act of jetting well points in cause damage in a highly stratified soil system? This is an important question to answer since long term dewatering and water management of the segmental wall will be dependent in part on how much water is rising upwards from depth after construction.
My concern is that if the contractor installs additional well points (at varying tip depths) in an attempt to dry the site up for construction, additional damage to the soil strata may occur and more upward flows will be the end result. My thought at this point is that the area should be dewatered using a more gentle approach; namely shallow sump pits along that area to avoid breaching these deeper artesian layers.
What do you think about the dewatering and sand boil theory? Thanks for your comments about this!
P.S. There are other concerns that we have been addressing on the fly for this site too; namely a cantilever sheet pile wall that was installed by the contractor with no design or analysis...
Now, to provide room for a new development, the embankment will be replaced with a new reinforced segmental retaining wall.
A contractor came in and installed a sheet pile wall (believed to be about 20 feet in length), along with 2 inch PVC well points (believed to be about 20 feet long, screened on the bottom 5 feet) on the side of the sheet wall opposite of the proposed excavation for the new segmental wall. The location of the sheet wall was near the crest of the existing embankment at the top. The wells were installed by jetting in under high water pressure on approximate 3 to 4 feet centers. Prior to the pump being turned on, some artesian flow was observed in about 50% of the wells. This was not surprising based on the original soil boring information.
After the pump had been started and was running for a few days, the contractor excavated the area adjacent to the sheet pile wall down approximately 8 to 10 feet. They noticed that even with the pumps running, there were sand boils at some areas near the wall, and the area of the proposed retaining wall was generally wet.
We were called out to the site to help them understand why their dewatering system was not working. First of all, it was obvious to me that the well points were not doing the job for which they were intended. I believe the well points are probably pulling water from deeper aquifers that probably do not need to be dewatered in order to dry the site up. There are more shallow aquifers making it through and up and around the sheet wall that are not affected by the well points.
My opinion about the sand boils is this; while they may be result of natural discontinuities in the soil strata that are now exposed to air for the first time, I believe that the pressure of the jets may have aggravated the problem by weakening certain strata and ultimately causing more sand boils to form during excavation in that area than would have existed otherwise. What do you think of that? In your experience, have you seen the act of jetting well points in cause damage in a highly stratified soil system? This is an important question to answer since long term dewatering and water management of the segmental wall will be dependent in part on how much water is rising upwards from depth after construction.
My concern is that if the contractor installs additional well points (at varying tip depths) in an attempt to dry the site up for construction, additional damage to the soil strata may occur and more upward flows will be the end result. My thought at this point is that the area should be dewatered using a more gentle approach; namely shallow sump pits along that area to avoid breaching these deeper artesian layers.
What do you think about the dewatering and sand boil theory? Thanks for your comments about this!
P.S. There are other concerns that we have been addressing on the fly for this site too; namely a cantilever sheet pile wall that was installed by the contractor with no design or analysis...