Hi all,
I have a situation where there is an existing continuous, simply-supported 4"x12" (3.5"x11.25" field measured) wood beam. There is a column at approximately midspan. The beam is exposed (painted white to match ceiling and walls), and the owner wants the column removed because it interferes with the "flow" of the area. The beam supports a flat roof (2x6 rafters at 24" oc with 1/2" plywood sheathing, asphalt shingles, and 1/2" gypboard ceiling).
Using 10psf for dead load and 20 psf for live load and assuming the existing beam is made of douglas fir-larch #1 with a span (ctr of bearing to ctr of brg) of 24.6 feet and a tributary loading width of about 8 feet, I have determined that I can remove the column if I sandwich the existing 4x12 with either 2-7/8" x 11-7/8" Trus Joist 2.0E Paralam PSLs OR 1/2" x 11-1/4" steel plates on each side. The PSLs should keep the dead load deflection under 0.4" and the live load deflection under 0.6". I think the steel plates provide about the same, if not better (I don't have my calcs in front of me).
Does anyone have any opinions on what is the "better" option (wood or steel), regarding both common engineering practice and constructability (i.e., cost)? The owner, of course, would like the retrofit to be as thin as possible. Also, any advise regarding providing the additional steel or PSLs on the SAME side of the existing beam for aesthetic reasons, e.g., using a single 1" thick steel plate or a thicker piece of manufactured wood on one side only?
I've been designing concrete bridges for the past 10 years so I'm a little bit rusty on the latest in residential or light construction, as are all the other guys in my bridge design office. So, you're probably wondering why I'm doing this. Well, my mom asked me to so I felt obligated to look into it for her. If you think I should contact another engineer who specializes in this kind of stuff, please don't hesitate to let me know. The calcs seem pretty straightforward to me, though.
I have a situation where there is an existing continuous, simply-supported 4"x12" (3.5"x11.25" field measured) wood beam. There is a column at approximately midspan. The beam is exposed (painted white to match ceiling and walls), and the owner wants the column removed because it interferes with the "flow" of the area. The beam supports a flat roof (2x6 rafters at 24" oc with 1/2" plywood sheathing, asphalt shingles, and 1/2" gypboard ceiling).
Using 10psf for dead load and 20 psf for live load and assuming the existing beam is made of douglas fir-larch #1 with a span (ctr of bearing to ctr of brg) of 24.6 feet and a tributary loading width of about 8 feet, I have determined that I can remove the column if I sandwich the existing 4x12 with either 2-7/8" x 11-7/8" Trus Joist 2.0E Paralam PSLs OR 1/2" x 11-1/4" steel plates on each side. The PSLs should keep the dead load deflection under 0.4" and the live load deflection under 0.6". I think the steel plates provide about the same, if not better (I don't have my calcs in front of me).
Does anyone have any opinions on what is the "better" option (wood or steel), regarding both common engineering practice and constructability (i.e., cost)? The owner, of course, would like the retrofit to be as thin as possible. Also, any advise regarding providing the additional steel or PSLs on the SAME side of the existing beam for aesthetic reasons, e.g., using a single 1" thick steel plate or a thicker piece of manufactured wood on one side only?
I've been designing concrete bridges for the past 10 years so I'm a little bit rusty on the latest in residential or light construction, as are all the other guys in my bridge design office. So, you're probably wondering why I'm doing this. Well, my mom asked me to so I felt obligated to look into it for her. If you think I should contact another engineer who specializes in this kind of stuff, please don't hesitate to let me know. The calcs seem pretty straightforward to me, though.