I have to design a small lift station for a church in Georgia. Does anyone know what kind of flowrate I should use to size the pump?
If I go with the Georgia Septic Manual Flow of 7 GPD/Seat, I get 6300 GPD for a 900 seat sanctuary; which is 4.4 GPM. With a peaking factor of 4, that gives me 17.6 GPM. That seems a little low.
If I assume a 4 hour day instead of 24 hour day, I get 26.25 GPM. With a peaking factor of 4, that gives me 105 GPM.
Flow Based on Fixture count is 135 GPM if everything is running at one time.
I am thinking I'll use the 105 GPM for the pump but I hate to oversize the pump and have the church pay more. Any experience/feedback will be appreciated.