Saturated or Unsaturated Impedance

Status
Not open for further replies.

davva

Marine/Ocean
Sep 27, 2004
99
I've tried a search on this forum to find some of the answers.

When considering electrical calcs, should unsaturated or saturated generator reactance be used for:-

1. Harmonic Analysis

2. Short Circuit Calcs

3. Motor Starting Volt drop calcs

From what I've read there appears to be an answer to 2 and 3 above, but not to 1...

1. ??? (unsaturated data?)

2. Saturated data

3. Unsaturated data

I stand to be corrected on my interpretation on the above answers!







 
Replies continue below

Recommended for you

davva
You are correct

Generally speaking saturated values are used where the current is high - ie fault calculations. Unsaturated values are used up to rated current ie motor starting calcs. I would use unsaturated for harmonic calcs.
 