eeprom, there is no documentation that the SCCR is based on a three-phase fault or a single-phase fault. It does not matter, it is a single number.
Do your fault current analysis, determine what the highest available fault current will be (note: single-line-to-ground is often the highest if the system is solidly grounded, depending on the ratio of positive sequence impedance zero sequence impedance). Choose your equipment with an SCCR that is above the highest available fault current.
One more try at an example:
A device has an SCCR of 10kA. The (grounded Y) system fault current calculations indicate that a bolted three-phase fault will produce 9.8kA, and a single-line to ground fault will produce 10.5kA. The device is not suitable, because a single-line to ground fault will exceed its SCCR rating.
Another device has an SCCR of 10kA. The (ungrounded delta) system fault current calculations indicate that a bolted three-phase fault will produce 9.8kA. In this case, the single-line-to-ground fault is zero, and the two-phase fault is much less than the three-phase value. So 9.8kA is the maximum available, and the device is suitable.
The point is that both of those devices have three phases connected to them. The SCCR of the devices must be higher than the highest amount of current that will pass through any of the three connections.
In sum, the SCCR is not based on a three-phase fault or a single-phase fault. It is to be applied to the highest available current that can flow through any one terminal. A current exceeding the SCCR through one terminal of a three-phase device will probably destroy it. A current exceeding the SCCR through two or three of its terminals will also probably destroy it.
"Highest Available Fault Current" not three-phase, not single-phase. Whichever is higher.