Hi,
I don't think there is specific emebedment minimum depth requirement for screw pile to work other than frost depth and uplift capacity requirement. But I am not 100%.
I got a project, minimum torque specified was 80,000 ftlb and depth of installation was around 24 feet. But contractor was saying they got 100,000 ftlb and was not able to go further than 12 feet because of rock. I did not get chance to look for there reading data sheet yet. soil was mainly stiff to very stiff clay.
will the installation be fine to take design loads using torque and capacity relation? people may argue why not. Do we need to satisfy design depth and minimum torque both?
Will appreciate for your insight on this.
Thanks.
I don't think there is specific emebedment minimum depth requirement for screw pile to work other than frost depth and uplift capacity requirement. But I am not 100%.
I got a project, minimum torque specified was 80,000 ftlb and depth of installation was around 24 feet. But contractor was saying they got 100,000 ftlb and was not able to go further than 12 feet because of rock. I did not get chance to look for there reading data sheet yet. soil was mainly stiff to very stiff clay.
will the installation be fine to take design loads using torque and capacity relation? people may argue why not. Do we need to satisfy design depth and minimum torque both?
Will appreciate for your insight on this.