I am having good results with a sealed attic in the tropics.
Roof is externally insulated about R7, and utilizes white metal above insulation to reflect the heat away. Gable walls internally insulated.
Attic is unconditioned, however it is separated from the conditioned space by a mere layer of dry wall. So there is some sensible heat transfer still as there are a few degrees of temperature differential, and mositure is passing through the ceiling as well to the dry air below.
Attic is behaving like a plenum space in a commercial building with a roof deck and no ventilation.
If I keep my conditioned space at 75F, RH is down to a pretty solid 40%, attic above averages 81F @51%RH, makes ASHRAE's comfort zone.
I shut system off for several hours via a high day time temperature set back. Ambient air held steady with a dewpoint of about 78.8 over this time frame and after four hours time, the rise in indoor RH was minimal, suggesting low, low natural infiltration rate.
Minimal insulation, keeping the heat out in the first place, sealed attic seems to be blowing the doors off of a hot sauna above a thick layer of fibreglass. Bring on the pot lights now.
Take the "V" out of HVAC and you are left with a HAC(k) job.
Roof is externally insulated about R7, and utilizes white metal above insulation to reflect the heat away. Gable walls internally insulated.
Attic is unconditioned, however it is separated from the conditioned space by a mere layer of dry wall. So there is some sensible heat transfer still as there are a few degrees of temperature differential, and mositure is passing through the ceiling as well to the dry air below.
Attic is behaving like a plenum space in a commercial building with a roof deck and no ventilation.
If I keep my conditioned space at 75F, RH is down to a pretty solid 40%, attic above averages 81F @51%RH, makes ASHRAE's comfort zone.
I shut system off for several hours via a high day time temperature set back. Ambient air held steady with a dewpoint of about 78.8 over this time frame and after four hours time, the rise in indoor RH was minimal, suggesting low, low natural infiltration rate.
Minimal insulation, keeping the heat out in the first place, sealed attic seems to be blowing the doors off of a hot sauna above a thick layer of fibreglass. Bring on the pot lights now.
Take the "V" out of HVAC and you are left with a HAC(k) job.