Aug 30, 2019 #1 bpiermat Structural Mar 7, 2006 44 0 0 US For rebar development into the superstructure from the column is it correct include full length, or does the cover on the superstructure need to be neglected? For seismic analysis. Zone D Thanks!
For rebar development into the superstructure from the column is it correct include full length, or does the cover on the superstructure need to be neglected? For seismic analysis. Zone D Thanks!
Aug 31, 2019 #2 Agent666 Structural Jul 2, 2008 3,080 0 0 NZ Generally the development length for development is taken from the face of the member so includes the cover (if that's what you are asking?) Upvote 0 Downvote
Generally the development length for development is taken from the face of the member so includes the cover (if that's what you are asking?)