Dear Forum Members,
My GSU transformer specification mentions that the " The transformer is required to demonstrate design and construction suitable for Seismic Zone 3, in conformance with IEEE Standard 693-2005."
The section 1.3 of IEEE Std 693-2005- IEEE Recommended Practice for Seismic Design of Substations mentions " If any part of this recommended practice is removed, not met, or reduced, then neither the user nor the manufacturer may claim the equipment is in compliance with IEEE Std. 693 and should not attach the seismic identification plate to the equipment."
Say the transformer is designed and constructed as per the IEEE Standard 693-1997. Does the manufacturer require to provide seismic plate to the transformer? Also, what kind of seismic information is required to be displayed on the seismic plate?
SG
My GSU transformer specification mentions that the " The transformer is required to demonstrate design and construction suitable for Seismic Zone 3, in conformance with IEEE Standard 693-2005."
The section 1.3 of IEEE Std 693-2005- IEEE Recommended Practice for Seismic Design of Substations mentions " If any part of this recommended practice is removed, not met, or reduced, then neither the user nor the manufacturer may claim the equipment is in compliance with IEEE Std. 693 and should not attach the seismic identification plate to the equipment."