Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Seismic load combination

Status
Not open for further replies.

SHBH

Structural
Mar 23, 2007
55
Hi,
I was checking cl 12.4.2.3 for seismic load combinations, in which 0.2Sds is used to account for the seismic load in vertical direction. For rest of the horizontal seismic loads , one can use 100% in X dir and 30% in Z dir (seismic design cat D).
What if 100% is in the vertical direction, should it then be 100%Vertical + 30% hor-X + 30%hor-Z
I have seen this combination to be used in some other design offices, but where is the ref in code.

 
Replies continue below

Recommended for you

100% Vert + 30%X + 30%Z?? No.

The primary seismic is always either X or Z. The vertical is just an added seismic effect that accompanies the X or Z.

 
I've seen something like this before and I think it could possibly have come from ASCE 4 for "Seismic Analysis of Safety-Related Nuclear Structures" although I can't find it in the spec now. It might have been in other contract specs.

Regards,
-Mike
 
Thanks JAE & Mikee,
From this discussion now i can remember that the 100% vertical seismic effect was really mentioned in the nuclear DBR.
so the eccence is vertical has to be 20% if i am using ASCE7 load comb.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor