Seismic Overturning Moment - in Tanks

Status
Not open for further replies.

Jacst3

Structural
May 3, 2010
22
I am considering the overturning moment on a tall steel tank (12' dia. X 43' high) filled with a dry product. This is a mild seismic area, so I am using ASCE 7-05, section 12.8 to find the Cs coefficient for the seismic shear equation V=CsW. My question is, even though I have a large overturning moment due to a seismic event, what part of the dead load of the product acts to counter the overturning moment? Would one simply use the total dead load of the product multiplied by the moment arm (centroid of tank to tank edge). This would totally void the seismic overturning moment due to the large amount dead load. I cannot find any direction in the code.

Thanks for any input!
 
Replies continue below

Recommended for you

If you assume it's full when you figure out your lateral forces, you can use that weight to resist overturning. Conversely for the empty case, no contents are included.
The codes are not a design suicide pact. You don't have to use the full case for lateral compared to the empty for resistance.
 
To see if there is any net overturning use the load combinations in section 12.4.2.3:
for strength design (0.9 - 0.2 SDS)D + ρE;
for ASD (0.6 - 0.14SDS)D - 0.7ρE
 
Generally, on a flat-bottom steel tank, the bottom is not designed to support the contents when not supported by soil from below.
In the liquid tank codes, a portion of the tank bottom near the shell is assumed to supply some resisting load due to tank contents, but the amount is limited based on tank diameter and properties of the bottom, and will not be anywhere near the total contents of the tank.
You could presumably use the same approach with a granular product. See AWWA D100 or API-650.

If the tank is anchored to a concrete slab or ringwall, then all of the contents above the slab or ringwall are assumed to resist seismic overturning of the foundation.

If the tank has a suspended/conical bottom, then the entire contents would be assumed to resist overturning as well. Possibly with some adjustment for vertical acceleration.
 