atrizzy
Structural
- Mar 30, 2017
- 362
Howdy folks, I posted this over in HVAC but I don't think they're keen.
I'm a structural engineer looking for a bit of input from you HVAC folks experienced with the West Coast of Canada.
Are there any guides or codes that need to be followed in addition to the requirements of NBCC 4.1.8.18 for restraining ductwork, sprinkler piping, etc? Or is this stuff typically allowed to swing and deflect providing nothing is at risk of damage and that the anchorage is 2x what's required for vertical support?
The NBCC seismic components of buildings clause above seems appropriate for heavy units, AHUs, pumps, etc if suspended from a ceiling, but it seems a little stringent for ducts and small, light pipes.
What do you say? And thanks in advance!
I'm a structural engineer looking for a bit of input from you HVAC folks experienced with the West Coast of Canada.
Are there any guides or codes that need to be followed in addition to the requirements of NBCC 4.1.8.18 for restraining ductwork, sprinkler piping, etc? Or is this stuff typically allowed to swing and deflect providing nothing is at risk of damage and that the anchorage is 2x what's required for vertical support?
The NBCC seismic components of buildings clause above seems appropriate for heavy units, AHUs, pumps, etc if suspended from a ceiling, but it seems a little stringent for ducts and small, light pipes.
What do you say? And thanks in advance!