I have a question of designing seismic separation joint:
When sizing for seismic separation joint or expansion joint between 2 buildings, should we amplify the cracked deflection of a concrete building by Cd factor in Table 9.5.2.2? The building’s cracked deflection is produced by applying the crack factor prescribed in ACI 318 by using ETABS and Pdelta Analysis.
ASCE 7-02 Section 9.1, under “DISPLACEMENT” – “Total maximum displacement” specifies that: “The maximum considered earthquake lateral displacement, including additional displacement due to actual and accidental torsion, required for…design of building separations and vertical load testing of isolator unit prototype.”
Question:
1) It appears that for the design of building separation, the amplification factor, Cd, in Table 9.5.2.2 is not required. Is this correct?
2) For seismic displacement, are we allowed to use the stiffness increase as specified in ACI 318 Section R10.11? Which specifies that: “Analyses of deflections, vibrations, and building periods are needed at various service load levels…it is satisfactory to use 1/0.7 = 1.43 times the moments of inertia given in 10.11.1 for service load analyses.”
Thank you for your help.
When sizing for seismic separation joint or expansion joint between 2 buildings, should we amplify the cracked deflection of a concrete building by Cd factor in Table 9.5.2.2? The building’s cracked deflection is produced by applying the crack factor prescribed in ACI 318 by using ETABS and Pdelta Analysis.
ASCE 7-02 Section 9.1, under “DISPLACEMENT” – “Total maximum displacement” specifies that: “The maximum considered earthquake lateral displacement, including additional displacement due to actual and accidental torsion, required for…design of building separations and vertical load testing of isolator unit prototype.”
Question:
1) It appears that for the design of building separation, the amplification factor, Cd, in Table 9.5.2.2 is not required. Is this correct?
2) For seismic displacement, are we allowed to use the stiffness increase as specified in ACI 318 Section R10.11? Which specifies that: “Analyses of deflections, vibrations, and building periods are needed at various service load levels…it is satisfactory to use 1/0.7 = 1.43 times the moments of inertia given in 10.11.1 for service load analyses.”
Thank you for your help.