Mbrooke
Electrical
- Nov 12, 2012
- 2,546
When can a substation get away without having breaker failure relays?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
"First, a distinction needs to be made between static and
reconfigurable buses. In reconfigurable buses, a given breaker
may connect a given network element (e.g., line, transformer,
capacitor bank) to multiple bus sections. Examples of
reconfigurable buses include a double-bus single-breaker or
main/transfer bus. This dynamic association of breakers
complicates the BF tripping logic because the BF protection
system must know which breakers are connected to the same
bus as the failed breaker. For this reason, the BF function is
often integrated with a low-impedance bus protection system,
or the bus protection system receives the BFT signals from
external BF elements and routes the BFT command
adequately to the appropriate breakers"
DTR2011 said:In my neck of the woods, a separate BF seems to be preferred. It ranges from a SEL 501 to a SEL-352 to SEL-451 in newer installations. Most applications are ring bus. In all cases, the BF relay trips the bus diff lock out (86B). I have seen some applications of a dedicated 86BF device, but not in newer designs.
I have also seen SEl-421/411L/311L 321/311C schemes where 50BF & 79 is implemented into the relays to trip the 86B/86BF. The advantage I see from this scheme is that an entire protection system (Primary or backup) can be taken out of service for maintenance / modifications, without the loss of BF protection. It makes things a bit easier to explain to system operations that only the primary, or back up protection will be out of service, when starting work. Generally with the Transco this is straightforward, but if dealing with other entities such as Genco (Nuclear especially), having all parties aware that all functionality is in place is a statement most like to hear.
As far as reducing testing errors, yes it can occur, but if a BF trip from an IED that does it internally, or one that just initiates a dedicated relay, in either case the schematic was not analyzed and all trips or initiates were not pulled.