Dear Friends.
Sorry for such kind of Q's.
I must connect SEL311L in my application, its decided today before few hours.
We don't have any expirience with SEL, we don't have any local support.
Setting, software, commissioning, no problem, we have enough time.
I need urgently few issues.
CT data, according to manual.
1. 150>=(X/R+1) x If x Zb
2. 20>= (X/R+1) x If x Zb ( for avoid CT saturation entriely).
3. 7.5 times worse, than the case which avoid all CT satuaration.
I calculated my CT before, for another relay with 21 with 79.
My chioce was class PX Vk=1500V, Rct<=4Ohm.
X/R=40, 63kA, CT: 3000/1A.
that means If=21, 41x21>>>>>150.
What is a point???
Next issue.
OUT107 can operated as extra alarm.
What means? Its LIVE-CONTACT, Im not found any data about live-contact or WD contact or Internal relaya fault contact.
Next issue, according to my understanding, all inputs and outputs of SEL311L if free programmable. Its true?
My problem is re-design of protection cubicle, all was ready for another relay, and next week need start mnf. of cubicle.
Thanks in advance.
Best Regards.
Slava
Sorry for such kind of Q's.
I must connect SEL311L in my application, its decided today before few hours.
We don't have any expirience with SEL, we don't have any local support.
Setting, software, commissioning, no problem, we have enough time.
I need urgently few issues.
CT data, according to manual.
1. 150>=(X/R+1) x If x Zb
2. 20>= (X/R+1) x If x Zb ( for avoid CT saturation entriely).
3. 7.5 times worse, than the case which avoid all CT satuaration.
I calculated my CT before, for another relay with 21 with 79.
My chioce was class PX Vk=1500V, Rct<=4Ohm.
X/R=40, 63kA, CT: 3000/1A.
that means If=21, 41x21>>>>>150.
What is a point???
Next issue.
OUT107 can operated as extra alarm.
What means? Its LIVE-CONTACT, Im not found any data about live-contact or WD contact or Internal relaya fault contact.
Next issue, according to my understanding, all inputs and outputs of SEL311L if free programmable. Its true?
My problem is re-design of protection cubicle, all was ready for another relay, and next week need start mnf. of cubicle.
Thanks in advance.