proznick
Electrical
- May 26, 2008
- 16
I am doing a ground grid study for a small islanded hydro facillity connected to a utillity diesel plant. Using ETAP to model the short circuit ground currents in the hydro plant substation (step and touch potentials).
In setting up the model for the utillity diesels, should the sub-transient current fault values provided by the utillity be used or the synchronous fault current values.
In designing ground grid for sub, worst case would be using sub-transient values.
When modeling the ground grid in ETAP, it wants "Fault Current" and the "X/R" ratio which makes me think that it wants the synchronous fault current and will compute the maximum sub-transient current level using th X/R ratio. If this is the case, when using the subtransient current value instead, will make for overdesigned ground grid size.
Any thoughts on this appreciated.
cheers,
RP
In setting up the model for the utillity diesels, should the sub-transient current fault values provided by the utillity be used or the synchronous fault current values.
In designing ground grid for sub, worst case would be using sub-transient values.
When modeling the ground grid in ETAP, it wants "Fault Current" and the "X/R" ratio which makes me think that it wants the synchronous fault current and will compute the maximum sub-transient current level using th X/R ratio. If this is the case, when using the subtransient current value instead, will make for overdesigned ground grid size.
Any thoughts on this appreciated.
cheers,
RP