Sorry if this is being resent. The previous thread was accidently removed.
Problem: The existing 40 year old porcelain station class lightning arresters that are protecting a generator have failed and need replacing (one for each phase).
Generator info: I have a 13.8KV Hydro Generator (25MVA) multi-turn coil windings. The manufacture for the generator approximates the BIL of the generator to be close to 40KV with a rise time defined by figure 1 section 6.2 of IEEE 522 - 2004. The neutral of the generator is tied to a step-down transformer with a 36ohm resistor in parallel (low impedance grounding).
Arrester info: The existing lightning arresters are rated at 15KV and turn on at 24.75KV. The lightning arresters are in parallel with a 0.25uF capacitor (rated voltage 13.8KV). The 13.8KV lines go through a step-up transformer and then connect to the transmission lines.
Questions:
What is the rule of thumb for selecting a station class lightning arrester in this application?
When making a selection, how is the Duty Cycle voltage and the MCOV (max continuous operating voltage) considered in reference to the operating Line-to-Line 13.8KV?
Appreciate any input.
Problem: The existing 40 year old porcelain station class lightning arresters that are protecting a generator have failed and need replacing (one for each phase).
Generator info: I have a 13.8KV Hydro Generator (25MVA) multi-turn coil windings. The manufacture for the generator approximates the BIL of the generator to be close to 40KV with a rise time defined by figure 1 section 6.2 of IEEE 522 - 2004. The neutral of the generator is tied to a step-down transformer with a 36ohm resistor in parallel (low impedance grounding).
Arrester info: The existing lightning arresters are rated at 15KV and turn on at 24.75KV. The lightning arresters are in parallel with a 0.25uF capacitor (rated voltage 13.8KV). The 13.8KV lines go through a step-up transformer and then connect to the transmission lines.
Questions:
What is the rule of thumb for selecting a station class lightning arrester in this application?
When making a selection, how is the Duty Cycle voltage and the MCOV (max continuous operating voltage) considered in reference to the operating Line-to-Line 13.8KV?
Appreciate any input.