Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Selection of ground rods: What are the determining factors?

Status
Not open for further replies.

HuskyFC450

Mechanical
Oct 12, 2012
8
0
0
US
Customer has approximately (15) small "CONEX" lockers scattered on a paved lot. Each of these small storage containers have various types of commercial/industrial hazardous waste materials inside (ballasts, fluorescent lamps, empty spray paint cans, batteries, etc.} A few of these metal containers have been grounded with an individual ground per container (don't know why since there is no electrical service or electrical connections to any of these containers}. If by chance, there are requirements to ground such enclosures, how would I select the correct dimension of ground rod, i.e. 1/2" x 8' or 5/8" x 10' etc?

Tom
 
Replies continue below

Recommended for you

I'd say they need it for lightning protection.

Your grounding should be designed to have less than 25 ohm. Obviously this varies with moisture etc. so design on the safe side, measure resistance and add rods as needed.

this depends largely on rod depths, and soil. your 10'rod could be OK. You may encounter rock less than 1-'or have very dry soil and then you need more rods or need to drill through rock.
 
Status
Not open for further replies.
Back
Top