I have some queries with regard to selection of NGR( Neutral Grounding Resistor) and NGT( Neutral grounding transformer) in ungrounded grids of modern industrial power systems.
1) This type of delta connected systems will be at 6.6,11,22,33 or 66 kV voltages and the neutral current of NGT (fault current) selected is 1320 (6.6 kV) to 750A (33&66 KV) J&P Transformer Hand book (ed13.0,2007) . At any voltage level, how this current is selected? As I understand,these MV systems are usually low resistance grounded. Currents of 300-1500 A are seen selected. Is it based on safety angle( arc flash over) or damage to core of rotating,machine?
In Beeman's Handbook on Industrial Power system (1955) it is recommended as 25 % of the main transformer full load current. What is the current practice?
2) Earlier manuals suggest a rating of 30 sec for NGT &NGR, bur recently the ratings are based on 10 sec ratings. Is it due to the developments in protection relays? The equivalent rating of NGT based from short time rating was used to be selected from the Westinghouse T& D handbook.( 1940 vintage) Any latest guidelines?(Apart from IEEE 32-1972)Any equivalent IEC to IEEE 32?
3) How to select the "R" of NGT &NGR? Let us take an example. In case of a 6.6 kV system, let us select a L-G fault current limit of 300 A. The main Transformer 20 MVA with 6.6 kV delta secondary with full load current of 1760 A and impedance of 12.5 %. ie X1=0.125 pu. To limit current to 300 A nearly 38 ohms per phase will be required in NGT alone is used. We have several options . Select a NGR of 9 Ohms & NGT of 9 Ohms so as to get a net R of 13 ohms(9+j9) I felt this will be best as even with a damage /flashover in NGR ,the over current will be limited in NGT.Or from cost angle, one should go for say 2 ohms for NGT &12 Ohms for NGR?
4) Beeman ( also IEEE) recommends X0/X1 less than 10 and R0/X0 more than 2 (R0=3 times R of NGR).What is the significance of these parameters?
Inviting guidance from experts.
1) This type of delta connected systems will be at 6.6,11,22,33 or 66 kV voltages and the neutral current of NGT (fault current) selected is 1320 (6.6 kV) to 750A (33&66 KV) J&P Transformer Hand book (ed13.0,2007) . At any voltage level, how this current is selected? As I understand,these MV systems are usually low resistance grounded. Currents of 300-1500 A are seen selected. Is it based on safety angle( arc flash over) or damage to core of rotating,machine?
In Beeman's Handbook on Industrial Power system (1955) it is recommended as 25 % of the main transformer full load current. What is the current practice?
2) Earlier manuals suggest a rating of 30 sec for NGT &NGR, bur recently the ratings are based on 10 sec ratings. Is it due to the developments in protection relays? The equivalent rating of NGT based from short time rating was used to be selected from the Westinghouse T& D handbook.( 1940 vintage) Any latest guidelines?(Apart from IEEE 32-1972)Any equivalent IEC to IEEE 32?
3) How to select the "R" of NGT &NGR? Let us take an example. In case of a 6.6 kV system, let us select a L-G fault current limit of 300 A. The main Transformer 20 MVA with 6.6 kV delta secondary with full load current of 1760 A and impedance of 12.5 %. ie X1=0.125 pu. To limit current to 300 A nearly 38 ohms per phase will be required in NGT alone is used. We have several options . Select a NGR of 9 Ohms & NGT of 9 Ohms so as to get a net R of 13 ohms(9+j9) I felt this will be best as even with a damage /flashover in NGR ,the over current will be limited in NGT.Or from cost angle, one should go for say 2 ohms for NGT &12 Ohms for NGR?
4) Beeman ( also IEEE) recommends X0/X1 less than 10 and R0/X0 more than 2 (R0=3 times R of NGR).What is the significance of these parameters?
Inviting guidance from experts.