ShaikhSahab
Electrical
- Dec 8, 2010
- 3
We are installing 49.5 MW wind power project. Wind Turbine Generators are Double Fed asynchronuos Generator, wound rotor. WTG will import power from Grid for excitation. We will produce power at 690Volts and evacute to power purchaser at 132kV level.
What will be Vector Group of GSU Transformer to step up from 690v/22kV and then power Transformer from 22kV / 132kV. Here is a confusion
If we select power transformer YnD11 (Yn at 132kV side and D at 22kV side) then how earth fault at 22kV Delta side will be sense during import of power from Grid?
If we select power transformer DYn11 (D at 132kV side and Yn at 22kV side) then how earth fault at 132kV Delta side will be sense during export of power to Grid?
I propose two solutions
1- Yn Yn 11 to protect both sides in any senario importing / exporting power from / to Grid.
2- YnD11 with earthing trasnformer (But it is very costly solution and extra switchgear/protection of earthing trasnformer will be required.
Please see this link on which i have uploaded diagram of different scenarios for your better understanding
Expert comments are requested to all for selection of best economical solution. Thanks
What will be Vector Group of GSU Transformer to step up from 690v/22kV and then power Transformer from 22kV / 132kV. Here is a confusion
If we select power transformer YnD11 (Yn at 132kV side and D at 22kV side) then how earth fault at 22kV Delta side will be sense during import of power from Grid?
If we select power transformer DYn11 (D at 132kV side and Yn at 22kV side) then how earth fault at 132kV Delta side will be sense during export of power to Grid?
I propose two solutions
1- Yn Yn 11 to protect both sides in any senario importing / exporting power from / to Grid.
2- YnD11 with earthing trasnformer (But it is very costly solution and extra switchgear/protection of earthing trasnformer will be required.
Please see this link on which i have uploaded diagram of different scenarios for your better understanding
Expert comments are requested to all for selection of best economical solution. Thanks