Situation:
Main control panel has a breaker rated at 1600A and several downstream 200A breakers with 100HP motor loads of 113FLA
The main breaker has Adjustable trips for Long, Short, Instantaneous and Ground fault.
The long, short and GF Have time adjustment as well
This breaker comes with everything set at minimum except the long trip set at max (1600A)
When a motor load was started, the main breaker tripped on instantaneous. The branch breaker did not trip.
The inst setting was set to a higher level and that solved the problem for testing purposes. What I really need to know is where to find documentation/ references which say this is alright to do. They are square d breakers and I can find the trip curves but no guidelines, or better yet, calculations for determining the LSIG settings to use for the main breaker. Any tips on selective coordination would be appreciated.
Main control panel has a breaker rated at 1600A and several downstream 200A breakers with 100HP motor loads of 113FLA
The main breaker has Adjustable trips for Long, Short, Instantaneous and Ground fault.
The long, short and GF Have time adjustment as well
This breaker comes with everything set at minimum except the long trip set at max (1600A)
When a motor load was started, the main breaker tripped on instantaneous. The branch breaker did not trip.
The inst setting was set to a higher level and that solved the problem for testing purposes. What I really need to know is where to find documentation/ references which say this is alright to do. They are square d breakers and I can find the trip curves but no guidelines, or better yet, calculations for determining the LSIG settings to use for the main breaker. Any tips on selective coordination would be appreciated.