Self storage warehouse facility

Status
Not open for further replies.

Chris RAN

Mechanical
Jun 13, 2019
2
Good afternoon,
I am looking to provide design criteria for a +/- 5050 sq. ft. warehouse that will contain self-storage containers.
The building is steel frame construction, 31 ft maximum roof height with a less than 1 on 12 roof slope.
The 5’ by 7’ by 7’ tall containers are primarily made of ¾” pressure treated plywood with a base of a large pallet. There is a solid plastic top and a poly-vinyl wrap / cover for weather protection. The containers are expected to be stacked 3 containers high (21 feet).
A company representative had mentioned to me that the containers may be shrink-wrapped prior to shipping, and there is the potential for future containers to be made of fiberglass. I would like to anticipate the worst-case scenario for the design criteria.

I would appreciate any guidance or experience you may have with a similar situation.

Thank you,
Chris
 
Replies continue below

Recommended for you

What solution did you find to this problem? How ar the pods lifted in place? Are they stable in the case of a forklift bump?
 
I think you are looking at rack storage of a Class IV commodity at best but I would lean to a rack storage of a Class A commodity.

TABLE 23.4.2 ESFR Protection of Palletized and Solid-Piled Storage of Group A Plastic Commodities

If you can keep the max height to 30'-0" you could use a K25.2 ESFR pendent sprinkler discharging at just 15 psi or 97.6 gpm for a total demand of around 1,450 gpm which includes hose stream.

Those self storage pods are going to have a lot of mattresses and upholstered furniture. I know many designers, myself included, would like to talk it into being a Class III commodity but that isn't reality in todays plastic world.

Stookey pointed out years ago how a Carhart jacket was manufactured of all plastic. Just because it looks like cotton doesn't make it cotton.
 
Cartoned Unexpanded Group A Plastic. Your design scope should exclude hazardous materials classified as flammable and combustible liquids, flammable gases, oxidizers, organic peroxides, unstable (reactive), water reactive, fireworks and explosives.
 
Stookey,

Why wouldn't it be an Expanded Group A plastic?

Table A.20.4(b).

Table 21.3.3(a) for buildings not exceeding 32'.

I would love to know the percentage by volume where storage is mattresses and upholstered furniture.

 