I have questions regarding how a fan coil unit's capacity changes with the Dry Bulb temperature of the air entering it.
DBE: Dry Bulb Temperature of air entering coil (F)
DR: Wet Bulb Depression Ratio
I am trying to select a unit from a catalogue and the following correction equation is given to get the unit's capacity at a DBE different than the one that the figures in the performance table are based on.
Correction Factor = 1.08 x CFM x(1-DR)x(New DBE - 80) , where 80 is the DBE the performance table is based on.
I noticed that increasing DBE results in a higher unit capacity, as opposed to my expectations which were that the higher the temperature of the air entering the unit, the less capacity it should be able to handle.
Based on this, just theoretically speaking, if I have a room that has a certain heat load, and my fan coil unit's capacity falls just short of this heat load, I can overcome the shortage in capacity by injecting hot air from the outside to raise the return air stream's dry bulb temperature? Is the hotter air adding energy to the refrigeration cycle somewhere?
My other question is the catalogue does not specify which capacity, sensible or latent is the one affected by the change in DBE. I'm assuming it is added on to the sensible capacity since it's a factor of DBE with no change in latent capacity. Is this true?
Thank you.
I have questions regarding how a fan coil unit's capacity changes with the Dry Bulb temperature of the air entering it.
DBE: Dry Bulb Temperature of air entering coil (F)
DR: Wet Bulb Depression Ratio
I am trying to select a unit from a catalogue and the following correction equation is given to get the unit's capacity at a DBE different than the one that the figures in the performance table are based on.
Correction Factor = 1.08 x CFM x(1-DR)x(New DBE - 80) , where 80 is the DBE the performance table is based on.
I noticed that increasing DBE results in a higher unit capacity, as opposed to my expectations which were that the higher the temperature of the air entering the unit, the less capacity it should be able to handle.
Based on this, just theoretically speaking, if I have a room that has a certain heat load, and my fan coil unit's capacity falls just short of this heat load, I can overcome the shortage in capacity by injecting hot air from the outside to raise the return air stream's dry bulb temperature? Is the hotter air adding energy to the refrigeration cycle somewhere?
My other question is the catalogue does not specify which capacity, sensible or latent is the one affected by the change in DBE. I'm assuming it is added on to the sensible capacity since it's a factor of DBE with no change in latent capacity. Is this true?