tmartin125
Mechanical
- May 27, 2011
- 43
ASHRAE and SNAME T&R 4-16 (2015) use a formula for sensible heat gain from equipment operated by electric motors as follows: q_em = 2545*(P/E_M)*F_UM*F_LM
where
q_em = heat equivalent of equipment operation, Btu/h
P = motor power rating, hp
E_M = motor efficiency, decimal fraction <1.0
F_UM = motor use factor, 1.0 or decimal fraction <1.0
F_LM = motor load factor, 1.0 or decimal fraction <1.0
2545 = conversion factor, Btu/h·hp
The attached exampled 15 hp ballast pump, using SNAME or ASHREA and a UF of 1 the result is 41951 bth/h.
Using actual heat gain the result is 2950 btulh.
The energy going into the motor is 36722 btu/h.
How can the energy from motor heat gain to the space be more than the energy going into the motor?