Sensible heat gain of electric motors

Status
Not open for further replies.

tmartin125

Mechanical
May 27, 2011
43
ASHRAE and SNAME T&R 4-16 (2015) use a formula for sensible heat gain from equipment operated by electric motors as follows: q_em = 2545*(P/E_M)*F_UM*F_LM

where
q_em = heat equivalent of equipment operation, Btu/h
P = motor power rating, hp
E_M = motor efficiency, decimal fraction <1.0
F_UM = motor use factor, 1.0 or decimal fraction <1.0
F_LM = motor load factor, 1.0 or decimal fraction <1.0
2545 = conversion factor, Btu/h·hp

The attached exampled 15 hp ballast pump, using SNAME or ASHREA and a UF of 1 the result is 41951 bth/h.

Using actual heat gain the result is 2950 btulh.

The energy going into the motor is 36722 btu/h.

How can the energy from motor heat gain to the space be more than the energy going into the motor?
 
 https://files.engineering.com/getfile.aspx?folder=71e12815-6481-4e72-81b8-4bbaf18d0e74&file=Motor_Heat_to_Space.xlsx
Replies continue below

Recommended for you

Hello,

How did you obtain the actual heat gain? Is that from the manufacturer's catalogue?

My old (2001) ASHRAE Fundamentals Book shows the instantaneous heat gain from a 15-hp motor as 44,400-btuh based on F_um=1.0 and F_lm=1.0, with the motor and driven equipment being located within the conditioned space. This is also based on a 3-Phase, 1750-rpm, 86% efficient open-drip-proof motor. If your system is known to run infrequently or under-loaded, you can take some reduction via F_um and F_lm (which it looks like you did in one of your calcs where you came up with approx 1-ton as a load using a F_UM=0.3).

I had a project with a fire pump where, based on fire pump testing standards, was able to reduce the instantaneous heat gain from the 60-hp motor (172-MBH) to something much less since the pumps are tested weekly, only for a certain amount of time, and at dead head. I was originally going to provide a cooling system for the fire pump room before a senior engineer talked me off of the ledge.

Also see: