michalakis
Electrical
- Oct 7, 2002
- 2
In our electric utility we have been using Sensitive Earth Fault (SEF) relays for the protection of the 11 kV overhead distribution lines, and they are set for operation at 6 Amps and 5 seconds time delay.
Their purpose is to detect fallen conductors of o/h lines. We provide this protection additionally to normal Overcurrent and Earthfault relays.
When such a SEF relay operates, because of fear to create conditions for a possible death accident, we proceed very carefully and carry out a complete and detailed patrol of the faulted o/h line to locate the fault and repair it before attempting to reenergise the feeder. This process is, of course, both very time-consuming and costly. The consumers thus affected may remain without supply usually for more than 8 hours.
However, there are occasions where a SEF relay operates not because of a fallen conductor (whose handling is so difficult) but because of a fault on a pole-mounted distribution transformer whose 11kV-side fuses (20Amps, fast type)do not operate to isolate the fault.
Our 11 kV lines, being 3-phase, 3-wire, 50 Hz and usually very lengthy with many branches, are supplied from substation transformers with secondaries y-connected and their neutrals solidly earthed. The 11 kV lines supply 3-phase Dyn11, 11000/433 V distribution transformers ranging in capacity from 25 to 200 kVA each and with their neutral solidly earthed too. We operate the 11 kV feeders radially only.
We like to hear of experiences with SEF relays operation from utility engineers, or others regarding:
1. Settings adopted for such relays.
2. Whether they face similar SEF relays operation caused by reasons other than fallen line conductors. If yes, what procedure do they follow to restore the supply? Do they patrol the whole line before attempting to reenergise it, or what else?
3. Any suggestion to cope with the problem of SEF relay operation for reasons other than fallen conductors?
Thanks.
Their purpose is to detect fallen conductors of o/h lines. We provide this protection additionally to normal Overcurrent and Earthfault relays.
When such a SEF relay operates, because of fear to create conditions for a possible death accident, we proceed very carefully and carry out a complete and detailed patrol of the faulted o/h line to locate the fault and repair it before attempting to reenergise the feeder. This process is, of course, both very time-consuming and costly. The consumers thus affected may remain without supply usually for more than 8 hours.
However, there are occasions where a SEF relay operates not because of a fallen conductor (whose handling is so difficult) but because of a fault on a pole-mounted distribution transformer whose 11kV-side fuses (20Amps, fast type)do not operate to isolate the fault.
Our 11 kV lines, being 3-phase, 3-wire, 50 Hz and usually very lengthy with many branches, are supplied from substation transformers with secondaries y-connected and their neutrals solidly earthed. The 11 kV lines supply 3-phase Dyn11, 11000/433 V distribution transformers ranging in capacity from 25 to 200 kVA each and with their neutral solidly earthed too. We operate the 11 kV feeders radially only.
We like to hear of experiences with SEF relays operation from utility engineers, or others regarding:
1. Settings adopted for such relays.
2. Whether they face similar SEF relays operation caused by reasons other than fallen line conductors. If yes, what procedure do they follow to restore the supply? Do they patrol the whole line before attempting to reenergise it, or what else?
3. Any suggestion to cope with the problem of SEF relay operation for reasons other than fallen conductors?
Thanks.