vandax
Electrical
- Mar 13, 2002
- 15
Hi
Does anyone has experience with application of sensitive ground fault relay in the distribution line.
We just have an experienced that the neutral relay is not detect the fault (broken of 1 phase wire and lay down on the ground) in 13.8 kV distribution line (20 ohm grounded system).
Disturbance recorder indicate that the fault current was not adequate to force the relay to open the breaker.
After checking the relay, we know that the relay has been equipped with sensitive ground fault element, but we don't enough experience to apply it. I would apreciate your input, plus delta of this function.
Regards
Does anyone has experience with application of sensitive ground fault relay in the distribution line.
We just have an experienced that the neutral relay is not detect the fault (broken of 1 phase wire and lay down on the ground) in 13.8 kV distribution line (20 ohm grounded system).
Disturbance recorder indicate that the fault current was not adequate to force the relay to open the breaker.
After checking the relay, we know that the relay has been equipped with sensitive ground fault element, but we don't enough experience to apply it. I would apreciate your input, plus delta of this function.
Regards