Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sensors for heat treat ovens

Status
Not open for further replies.

VARUN555

Mechanical
Sep 23, 2020
4
Hello,

I have a question regarding sensors. We have heat treat ovens of temperature around 1000 F. The doors of the ovens are closed and the billets move on the conveyor. I wanted to know what kind of sensor can be used to detect the billets approaching the Unload door so that we don't bang the billets to the door and we get the signal on the indicator light about the end of travel. Also which sensor can be used to detect the temperature of the billets coming out of oven ( the billets are usually at a temperature of 900F

Thank you
 
Replies continue below

Recommended for you

Optical or infrared pyrometers.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
As for the hot billet not bashing the door I recommend a typical optical detector SET. One is the transmitter and one is the receiver. Put a hole on both sides of the tunnel and shine the beam thru the tunnel where the billet will interrupt the beam just ahead of the door. The transmitter and receiver stay outside in acceptable temperature areas. They can easily see 20 feet if needed.
Thru beam senders and recievers


Keith Cress
kcress -
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor