Sepam 1000 2
charlierod
71
Does anyone has an idea about where i can find a manual of MG's Sepam 1000?
This relay seems to discontinuated so i have not been able to find information about it.
Thanks for your comments
Charlierod
If you have no luck with Schneider's website, I have hard copies of Sepam 1000 ( replaced by Sepam 1000+ series ) catalogs "Sepam 1000 Series, Protection & Measurement" and "Sepam 1000 Substations,Busbars,Transformers and motors".
mnewman:
Up to know i've not been very lucky in finding information in the web, so it would be really helpful if i can get those catalogs from you. How can i contact you?
Here's some information read from the relay, i have some idea about its interpretation but due to the lack of exact information i haven't been able to correctly predict the operation of the equipment, if somebody can interpret this please tell me
Metering
IM1=817 A
IM2=817 A
IM3=765 A
TRIP1= 817 A
TRIP2= 800 A
TRIP3= 783 A
In= 1,2 kA
Ino = 1,2 kA
fn = 60 Hz
LATCH = YES
Relay
50N/51N
Curve = EIT (Extremely Inverse Time, IEC-C)
Iso = 180 A
to >= 200 ms
Io >>= 3,6 kA
to >>= 50 ms
50/51
Is = 1,2 kA
t >= 200 ms
I >>= 14,4 kA
t >>= 100 ms
Charlierod
re: Sepam 1000 ( note Sepam 1000+ ) catalogs.
Sorry for the delay in answering.
I have some old Sepam 1000 catalogs I can scan and send to you.
What info do you want and where do I email it?
Murray Newman
Thanks for your interest in helping me. Specifically i need information about protection functions which should be contained in the following documents:
Metering and Protection Functions (AC0396(1))
Control and Monitoring Functions (AC0396(1))
I wonder if there's a document related to maintenance, if so and if you have it please send it too.
You can send information to the following e-mail:
c_rodriguez@lycos.co.uk
Thanks for your help