My question deals mainly with the NEC.
When you are stepping down from 480 volts to 120/208 volts
This is down stream from the building service equipment.
I was taught that you ground the neutral (XO) at the tranfomer connetions. The grounding electrode conductor is attached to building steel (generally) and then connected to the neutral (XO) lug in the transformer.
Then the secondaries of the transformer are feeding a new 120/208 volt panel. And in this panel the equipment grounds are seperated from the neutral conductors. Two different terminal bars. That is how I was taught and I belive this to be the correct method.
However, I recently transferred to a new project where some of the experienced personnel see things differently.
They say that the neutrals and the equip. grounds should be tied together. Their reasoning is that it is a "new service" hence neutrals and grounds go together at the first means of disconnect(service). However, I don't think it should be considered a service, I belive it is a seperatedly derived system.
I would like some clearification on this matter, with code references to help me understand. Thanks, Chris J. Henson
new service
When you are stepping down from 480 volts to 120/208 volts
This is down stream from the building service equipment.
I was taught that you ground the neutral (XO) at the tranfomer connetions. The grounding electrode conductor is attached to building steel (generally) and then connected to the neutral (XO) lug in the transformer.
Then the secondaries of the transformer are feeding a new 120/208 volt panel. And in this panel the equipment grounds are seperated from the neutral conductors. Two different terminal bars. That is how I was taught and I belive this to be the correct method.
However, I recently transferred to a new project where some of the experienced personnel see things differently.
They say that the neutrals and the equip. grounds should be tied together. Their reasoning is that it is a "new service" hence neutrals and grounds go together at the first means of disconnect(service). However, I don't think it should be considered a service, I belive it is a seperatedly derived system.
I would like some clearification on this matter, with code references to help me understand. Thanks, Chris J. Henson
new service