- May 11, 2005
- 50
Hello to the group.
I've got a precast rectangular tank that I am trying to analyze. The tanks are cast in two sections, a top and a bottom. The slabs are integrelly cast with the walls, forming essentially a two-way slab with a continuous knee-wall around the perimeter. The tanks range in size, but normally around 7 feet wide, 12 feet long, and the "wall" sections are 45 inches tall. Two tanks are cast: a 4" slab top and a 6" slab top.
ACI 318-11 chapter 13 lists applicability to include slabs that are continuously supported by walls to consider those walls as a beam with infinite stiffness.
My question: the negative moment that I envision at the slabtop/wall interface due to being monolithically cast... if ignored, the resulting shear & moment would be conservative?
I understand that ACI 350 handles "environmental underground tanks." Does the ACI 350 approach differ greatly from the ACI 318 approach?
Or... since these tank tops are so small, would a modified Tee-Beam analysis be done for the edges, and a two-way slab analysis be done for that portion of slab that is not included in the "beam flanges"?
Thanks
___
Craig T. Bailey, PE, LLS
I've got a precast rectangular tank that I am trying to analyze. The tanks are cast in two sections, a top and a bottom. The slabs are integrelly cast with the walls, forming essentially a two-way slab with a continuous knee-wall around the perimeter. The tanks range in size, but normally around 7 feet wide, 12 feet long, and the "wall" sections are 45 inches tall. Two tanks are cast: a 4" slab top and a 6" slab top.
ACI 318-11 chapter 13 lists applicability to include slabs that are continuously supported by walls to consider those walls as a beam with infinite stiffness.
My question: the negative moment that I envision at the slabtop/wall interface due to being monolithically cast... if ignored, the resulting shear & moment would be conservative?
I understand that ACI 350 handles "environmental underground tanks." Does the ACI 350 approach differ greatly from the ACI 318 approach?
Or... since these tank tops are so small, would a modified Tee-Beam analysis be done for the edges, and a two-way slab analysis be done for that portion of slab that is not included in the "beam flanges"?
Thanks
___
Craig T. Bailey, PE, LLS