Suggestion: Normally, a manufacturer is selected first. Then, you obtain data from the manufacturer.
Impedances will vary according to the transformer winding connections.
See References:
1. Electrical Transmission and Distribution Reference Book, Westinghouse Electric Corp., e.g. 1964, Table 5 in the rear.
2. IEEE Std 241-1990 Table 34 indicates transformer design impedance of Z=6% for a transformer of your size and voltages.
Based on the above postings and References, impedances will be:
Z1=Z2=Z=6%
Z0=6% depending on the transfomer connection and grounding.