Recently jumped the fence and started working at a utility. I am still trying to get up to speed on rules and requirements for utilities. I am working on some projects where they are using a fuse and circuit breaker in series: the circuit breaker has too low of an interrupting rating for the application and they are claiming that the higher rated fuse is protecting it. I have not yet asked if this is a "tested combination" as I know it from the NEC; I'm not sure that they would even know what I was talking about. I snooped around the office and found an NESC. I'm not sure if it's the right section as this is my first time looking at the NESC but Section 171 for circuit breaker application states "Devices that are intended to interrupt fault current shall be capable of safely interrupting the maximum short-circuit current they are intended to interrupt, and for the circumstances under which they are designed to operate." There is no mention of a series rating here and my interpretation of that section is that each device must be fully rated. Is this incorrect? A larger question; are utilities free to use the NESC in whatever manner they please whereas non-utilities don't have a choice in following NEC requirements? Generally city or state governments adopt a cycle of the NEC as an ordinance, is this done with the NESC? Is it permissible to apply the up-over-down method in the utility world? This is for 480V service by the way (before service disconnect).