Looking for advice on server room cooling sizing. I'm hoping to get some unbiased opinions from other pros who aren't trying to sell me something.
---
Part A:
We are moving 129 servers (4 racks), each with a nameplate rating of 350W, into a small room. Based on our measurements, each server is pulling 200W at peak load -- or a total of 26kW for all systems. There are no windows, and no one will be permanently stationed in the room (only in there to service the equipment). I would like to have some room for expansion. According to my calculations, I would require around 8 tons of cooling. However, I'm getting wildly differing opinions from the pros about the size:-
1. Previous owner of equipment is specifying that he was using 4 tons.
2. HVAC Engineer is specifying - a 5 or 6 ton "Liebert" Unit
3. Data Aire Rep is specifying - a 8 ton air-cooled ceiling mount unit
4. Liebert Rep is specifying - 10 tons (possibly 2 - 5 ton units)
Any contractors/engineers out there agree with any of these numbers?
---
Part B:
The room is only 124 sq ft. It is a bit small, so I'm worried that the system might short cycle. There will be a LOT of air moving around in this room. I had a few contractors in yesterday, and one of them jokingly said I might have problems opening the door.
Any advice about this? I might be able to convince management to make the room bigger (knock down a few walls around it), but I need some compelling opinions. However, I'd rather not make the room any bigger.
Thanks!
---
Part A:
We are moving 129 servers (4 racks), each with a nameplate rating of 350W, into a small room. Based on our measurements, each server is pulling 200W at peak load -- or a total of 26kW for all systems. There are no windows, and no one will be permanently stationed in the room (only in there to service the equipment). I would like to have some room for expansion. According to my calculations, I would require around 8 tons of cooling. However, I'm getting wildly differing opinions from the pros about the size:-
1. Previous owner of equipment is specifying that he was using 4 tons.
2. HVAC Engineer is specifying - a 5 or 6 ton "Liebert" Unit
3. Data Aire Rep is specifying - a 8 ton air-cooled ceiling mount unit
4. Liebert Rep is specifying - 10 tons (possibly 2 - 5 ton units)
Any contractors/engineers out there agree with any of these numbers?
---
Part B:
The room is only 124 sq ft. It is a bit small, so I'm worried that the system might short cycle. There will be a LOT of air moving around in this room. I had a few contractors in yesterday, and one of them jokingly said I might have problems opening the door.
Any advice about this? I might be able to convince management to make the room bigger (knock down a few walls around it), but I need some compelling opinions. However, I'd rather not make the room any bigger.
Thanks!