Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Would anyone have guides or advice on how to set the breaker failure logic for an SEL387 relay used in a transformer differential application controlling two circuit breakers? The user manual briefly mentions breaker failure and SEL makes note that it can be created using word bits and variable timers however none appear to go into detail regarding that.
The desired outcome is to have independent BF for each 33 kv primary and 11kv secondary breaker, in addition to being able to initiate BF logic for each breaker (retrip + current timer / BFT) via an INXX1 and INXX2 contact respectively.
......
A question on the side- how necessary is it to initiate BF when a primary or secondary breaker is tripped via a relay outside its zone of protection? I ask because theoretically over current built into the XFRMR differential would pick up a fault outside the zone of protection.
Second, while I normally do not do this for line protection- would you guys agree in using 52A by itself as an indicator of breaker failure? The scenario that I have in my mind is a 33kv L-G bus fault being cleared via bus protection while having a 33kv XFRMR breaker stick. The stuck breaker CTs would not measure much current, but the 33kv buss would be kept in a state of over voltage due to the delta primary.
Here is the single line of the substation at hand:
The desired outcome is to have independent BF for each 33 kv primary and 11kv secondary breaker, in addition to being able to initiate BF logic for each breaker (retrip + current timer / BFT) via an INXX1 and INXX2 contact respectively.
......
A question on the side- how necessary is it to initiate BF when a primary or secondary breaker is tripped via a relay outside its zone of protection? I ask because theoretically over current built into the XFRMR differential would pick up a fault outside the zone of protection.
Second, while I normally do not do this for line protection- would you guys agree in using 52A by itself as an indicator of breaker failure? The scenario that I have in my mind is a 33kv L-G bus fault being cleared via bus protection while having a 33kv XFRMR breaker stick. The stuck breaker CTs would not measure much current, but the 33kv buss would be kept in a state of over voltage due to the delta primary.
Here is the single line of the substation at hand: