I'm wondering what others do when setting line relays at/near generation, looking onto the system away from the generation. In particular, setting backup protection - the traditional zone 3 or any overcurrent elements.
Historically we've essentially ignored the variability and set the relays like they were anywhere else in the system, everything in service and the generator impedance option set to subtransient. Well, it's easy enough to see that's probably right for a backup zone that will trip after 1 second. In the case I'm looking at at the moment, we have a 115kV line that has around 200MVA (nameplate) of generation behind it across 16 units at four plants. We might get most of that during the spring of a good water year, but by fall of a dry year it may be less than 70MVA of nameplate and only 4 or 5 units. Wildly different source strengths.
That 115kV line then terminates at a large station, on the low-side of a large (more than 300MVA) 30/115kV transformer. The standard criteria says that the third forward zone should be set to see past all that in-feed and reach the end of the longest line out of that station. That can wind up being further than the relay can reach.
Sequential tripping will get enough of the in-feed removed that the relay in question will reach as far as it needs to, but that can get rather ugly.
How do other people handle this type of situation?
Historically we've essentially ignored the variability and set the relays like they were anywhere else in the system, everything in service and the generator impedance option set to subtransient. Well, it's easy enough to see that's probably right for a backup zone that will trip after 1 second. In the case I'm looking at at the moment, we have a 115kV line that has around 200MVA (nameplate) of generation behind it across 16 units at four plants. We might get most of that during the spring of a good water year, but by fall of a dry year it may be less than 70MVA of nameplate and only 4 or 5 units. Wildly different source strengths.
That 115kV line then terminates at a large station, on the low-side of a large (more than 300MVA) 30/115kV transformer. The standard criteria says that the third forward zone should be set to see past all that in-feed and reach the end of the longest line out of that station. That can wind up being further than the relay can reach.
Sequential tripping will get enough of the in-feed removed that the relay in question will reach as far as it needs to, but that can get rather ugly.
How do other people handle this type of situation?