Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Ok, the perfected: In the event local bus bar differential is out of service; a fault on a bus bar section is cleared via a 10 cycle bi-directional delayed zone 1 on the bus coupler set at 10% impedance of the shortest line, and transmission lines attached to the faulted bus clears via either a 35 cycle remote zone 2 or a 15 cycle reverse local zone 3 (reaching into the bus). This works well and achieves selective coordination in a last resort effort- or older stations that do not yet have dedicated bus bar protection but are being retrofitted with numerical relays.
However, does anyone have any tips on setting the transformer over current? Would you use impedance reach or directional overcurrent and to what magnitude? Or just let everything clear as it likes?
If possible, I'd like to have transformers back-feeding the faulted 230kv bus section clear, while transformers pulling current off the unfaulted bus(es) remain in service even though they feed the same 69kv bus thats reverse feeding the transformers still attached to the faulted buss section.
However, does anyone have any tips on setting the transformer over current? Would you use impedance reach or directional overcurrent and to what magnitude? Or just let everything clear as it likes?
If possible, I'd like to have transformers back-feeding the faulted 230kv bus section clear, while transformers pulling current off the unfaulted bus(es) remain in service even though they feed the same 69kv bus thats reverse feeding the transformers still attached to the faulted buss section.