djcbgn
Civil/Environmental
- Feb 14, 2004
- 27
Hi,
I was asked to look at a new sewer pump station that is not performing as intended. The pumps are S&L suction lift pumps. This is a two pump series arrangement (attached) There is approximately 10,600 feet of 6inch pvc (sdr18) force main and about 19 feet of 4 inch suction pipe(20 max lift per S&L). The high point is at the pipe end (discharge manhole location).
Static Head= 177 feet (99'2-815')
Design Flow = 250 gpm
TDH (design) = 236’
Approx. Pump CL elevation 834. Pressure gauge at this elevation
During initial startup the contractor filled the pipe but during subsequent pump start the pump would run about 190 gpm at 90 psi and then stop. It did not seem like they hit dead head, the impellers were spinning according to the contractor but no there was no flow. When the pumps were off the static pressure was at 70 psi, which is correct. The contractor exercised the isolation valves and air release valves to make sure they were open and tried again with the same results. I estimated the dead head pressure on the discharge main to be around 106 psi.
The contractor then ran the pumps through the 4 inch emergency bypass with the valve throttled some and got about 275 gpm at 91 psi. The pump ran normal is this case. This flow and pressure is close to falling on the pump curve. Next they again ran the pumps through the bypass but throttled the valve until the pump dead headed at 106 psi.
I included my calculations with the system head curve and pump curve plotted. I am wondering if this could be air trapped in the line. There are 6 air release valve locations on the force main . There is an aerial stream crossing just downstream of the pump station and there was not an air valve at the pump station (or just outside of the pump station/see attached). If there is air constricting flow wouldn’t this show as increased pressure? I am unsure why the pumps stop pumping at 91 psi discharge pressure when dead head pressure is about 106 psi. I could add air release valve at the pump station, but wanted to see if anyone had any ideas to trying to isolate the problem areas.
Please let me know what you think. Thank for your input.
I was asked to look at a new sewer pump station that is not performing as intended. The pumps are S&L suction lift pumps. This is a two pump series arrangement (attached) There is approximately 10,600 feet of 6inch pvc (sdr18) force main and about 19 feet of 4 inch suction pipe(20 max lift per S&L). The high point is at the pipe end (discharge manhole location).
Static Head= 177 feet (99'2-815')
Design Flow = 250 gpm
TDH (design) = 236’
Approx. Pump CL elevation 834. Pressure gauge at this elevation
During initial startup the contractor filled the pipe but during subsequent pump start the pump would run about 190 gpm at 90 psi and then stop. It did not seem like they hit dead head, the impellers were spinning according to the contractor but no there was no flow. When the pumps were off the static pressure was at 70 psi, which is correct. The contractor exercised the isolation valves and air release valves to make sure they were open and tried again with the same results. I estimated the dead head pressure on the discharge main to be around 106 psi.
The contractor then ran the pumps through the 4 inch emergency bypass with the valve throttled some and got about 275 gpm at 91 psi. The pump ran normal is this case. This flow and pressure is close to falling on the pump curve. Next they again ran the pumps through the bypass but throttled the valve until the pump dead headed at 106 psi.
I included my calculations with the system head curve and pump curve plotted. I am wondering if this could be air trapped in the line. There are 6 air release valve locations on the force main . There is an aerial stream crossing just downstream of the pump station and there was not an air valve at the pump station (or just outside of the pump station/see attached). If there is air constricting flow wouldn’t this show as increased pressure? I am unsure why the pumps stop pumping at 91 psi discharge pressure when dead head pressure is about 106 psi. I could add air release valve at the pump station, but wanted to see if anyone had any ideas to trying to isolate the problem areas.
Please let me know what you think. Thank for your input.