I have an unusual problem which I wonder if anyone has ever seen before. I would appreciate some advice.
We have a 275/11kV station auxiliary transformer which has developed a fault on one of the HV bushings. These bushings are SF6-oil, Micafil type RTKG 275-1050/1250 rated for 1420A.
The failure mode is that SF6 is present in the transformer tank and collects in the Buchholz relay where it may be released and tested at the sample point. The gas is definitely SF6, and this is corroborated by the loss of SF6 pressure on the associated busbar gas zone. The conclusion at present is that the bushing has suffered mechanical failure of a seal and this is causing the gas leakage.
Questions:
I have never considered repairing a bushing seal before, so this is new territory to me. We have been informed that the bushing is a write-off and a replacement is required, although this would be to the advantage of the source of that information. As the bushing appears to be electrically sound, I'm hoping for some independent opinion. I am not remotely interested in a Heath-Robinson repair on the bushing - it must be done properly, or not at all.
The oil within the transformer (presumably) has a quantity of SF6 dissolved in it. I say presumably because I don't know the solubility of SF6 in mineral oil. Our oil lab's response was "you've got what in it?", but they are pursuing this information for us. Is dissolved SF6 likely to be removed using standard vacuum processing plant (Ilovac or similar)? I am reluctant to replace 33 tonnes of oil if it can be salvaged, but I'm equally reluctant to re-use oil of unknown characteristics in an important transformer.
We have a possible spare bushing which we can 'borrow' from another transformer, but I think the bushing may not have been stored in especially good conditions and may have been exposed to some degree of humidity. We intend to carry out a tan delta test on the bushing: on the assumption that it is degraded, it has been suggested that the bushing may be dried under vacuum in a similar manner to a motor winding prior to impregnation. I'm sceptical, but only from gut feeling. Any comments are appreciated.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!
We have a 275/11kV station auxiliary transformer which has developed a fault on one of the HV bushings. These bushings are SF6-oil, Micafil type RTKG 275-1050/1250 rated for 1420A.
The failure mode is that SF6 is present in the transformer tank and collects in the Buchholz relay where it may be released and tested at the sample point. The gas is definitely SF6, and this is corroborated by the loss of SF6 pressure on the associated busbar gas zone. The conclusion at present is that the bushing has suffered mechanical failure of a seal and this is causing the gas leakage.
Questions:
I have never considered repairing a bushing seal before, so this is new territory to me. We have been informed that the bushing is a write-off and a replacement is required, although this would be to the advantage of the source of that information. As the bushing appears to be electrically sound, I'm hoping for some independent opinion. I am not remotely interested in a Heath-Robinson repair on the bushing - it must be done properly, or not at all.
The oil within the transformer (presumably) has a quantity of SF6 dissolved in it. I say presumably because I don't know the solubility of SF6 in mineral oil. Our oil lab's response was "you've got what in it?", but they are pursuing this information for us. Is dissolved SF6 likely to be removed using standard vacuum processing plant (Ilovac or similar)? I am reluctant to replace 33 tonnes of oil if it can be salvaged, but I'm equally reluctant to re-use oil of unknown characteristics in an important transformer.
We have a possible spare bushing which we can 'borrow' from another transformer, but I think the bushing may not have been stored in especially good conditions and may have been exposed to some degree of humidity. We intend to carry out a tan delta test on the bushing: on the assumption that it is degraded, it has been suggested that the bushing may be dried under vacuum in a similar manner to a motor winding prior to impregnation. I'm sceptical, but only from gut feeling. Any comments are appreciated.
----------------------------------
If we learn from our mistakes,
I'm getting a great education!