Shaft Enclosure Fire Rated Walls On Roof Level

Status
Not open for further replies.

Waleed Ali

Mechanical
Apr 3, 2018
1
0
0
SA
I have central AC system & air ducts are coming from roof through one big shaft. We have so many air ducts coming from roof through the same shaft. My questions are:
1. Shall this shaft on roof covered and constructed with fire rated walls?
2. Shall we install fire dampers on air ducts penetrating the shaft walls on roof?
>>
>>
Much appreciated if you have a reference :)
 
Replies continue below

Recommended for you

This will be code dependent but external walls/roofs do not typically need to be fire rated. Fire rating is normally required to limit the spread of fire within a building.
I have on occasion seen requirements for fire rated external walls but this would normally only be when there is a large fuel tank or transformer sited adjacent to the building which would be a risk to the building if it were to catch fire.
 
From working on a similar type of project just like your scenario, only the shaft wall penetrations require fire/smoke dampers.
You should ask your local code official for their opinion.
 